Edit HVAC Zone data - Sequence

Data on the Sequence tab defines the load distribution scheme, heating and cooling calculation sequences and sequential heating and cooling fraction schedules.

Load Distribution Scheme

Load Distribution Scheme

Select the load distribution scheme to be used for this HVAC Zone. Choose from the following options:

 

Heating Calculation Sequence

Each item of zone heating equipment associated with the current HVAC zone is listed under the Heating Calculation Sequence header. Here you can define the order that each item of equipment is simulated and hence the sequence that each item of equipment will try to meet the demand with its available capacity.

 

Equipment is simulated in the order specified, depending on the current thermostat request. For equipment of similar type, assign sequence 1 to the first system intended to serve that type of load, assign sequence 2 to the next system, and so on. The #1 sequence equipment will try to meet the entire demand with its available capacity and then pass the results on to #2 to meet any remaining load and so on.

 

For situations where one or more equipment types has limited capacity or limited control capability, order the sequence so that the most controllable piece of equipment runs last. For example, with a dedicated outdoor air system (DOAS), the air terminal for the DOAS should be assigned a sequence of 1. Any other equipment should be assigned sequence 2 or higher so that it will see the net load after the DOAS air is added to the zone.

Cooling Calculation Sequence

Each item of zone cooling equipment associated with the current HVAC zone is listed under the Cooling Calculation Sequence header. Here you can define the order that each item of equipment is simulated and hence the sequence that each item of equipment will try to meet the demand with its available capacity.

 

Equipment is simulated in the order specified, depending on the current thermostat request. For equipment of similar type, assign sequence 1 to the first system intended to serve that type of load, assign sequence 2 to the next system, and so on. The #1 sequence equipment will try to meet the entire demand with its available capacity and then pass the results on to the #2 to meet any remaining load and so on.

 

For situations where one or more equipment types has limited capacity or limited control capability, order the sequence so that the most controllable piece of equipment runs last. For example, with a dedicated outdoor air system (DOAS), the air terminal for the DOAS should be assigned a sequence of 1. Any other equipment should be assigned sequence 2 or higher so that it will see the net load after the DOAS air is added to the zone.

Sequential Heating Fraction Schedules

For each item of zone heating equipment associated with the current HVAC zone, select a schedule that specifies the fraction of the remaining heating load this equipment will attempt to serve. This setting is only available if the Load distribution scheme is set to 1-Sequential Load.

Sequential Cooling Fraction Schedules

For each item of zone cooling equipment associated with the current HVAC zone, select a schedule that specifies the fraction of the remaining cooling load this equipment will attempt to serve. This setting is only available if the Load distribution scheme is set to 1-Sequential Load.